weird voltage readings
weird voltage readings
I came across weird volt readings in work today. Maybe someone has an explanation. Working with THREE PHASE 480V heaters. At the disconnect the voltage (when the disconnect was open) was 480V between any two legs. And 277V from any leg (3) to ground. But with the disconnect closed, voltage between one leg and ground was 0V and between one other leg and ground was @ 500V. Possibly what I thought was ground was not really ground? And there was no good ground?
The question is hard to answer because we don't know if the source is Delta or Wye connected. Same for the load. There also may be some confusion between Ground and Neutral Return conductors.
I suspect the load wires the Ground to one of the phases and uses that like a neutral. but I can only guess. If the heaters have different power settings, you may even see your readings change when you change the setting.
Best advice is to measure the resistance (continuity) between all leads on the load while it is disconnected (in other words, "Ohm it Out"). In the end, I don't quite understand why you would have more than 480V in any configuration.
I suspect the load wires the Ground to one of the phases and uses that like a neutral. but I can only guess. If the heaters have different power settings, you may even see your readings change when you change the setting.
Best advice is to measure the resistance (continuity) between all leads on the load while it is disconnected (in other words, "Ohm it Out"). In the end, I don't quite understand why you would have more than 480V in any configuration.
-
- Posts: 159
- Joined: Wed Oct 29, 2003 1:01 am
- Contact:
- Chris Smith
- Posts: 4325
- Joined: Tue Dec 04, 2001 1:01 am
- Location: Bieber Ca.
Who is online
Users browsing this forum: No registered users and 4 guests