3 phase welder

Post by Disco »

I have a Hobart Model R400 3 phase welder (230 or 460 vac). Can I parallel all three transformers and run on single phase? Or can I just fed one transformer and run at reduced output? This is a 400 amp welder with a mag amp control. I don't need 400 amps, 150 would probably be plenty. Looks like I could just use the transformer that feds the control circuit. I would have to feed the cooling fan separately, but that would not be a problem. Any thoughts?
User avatar
dacflyer
Posts: 4748
Joined: Fri Feb 08, 2002 1:01 am
Location: USA / North Carolina / Fayetteville
Contact:

Post by dacflyer »

we could tell you easier if you possibly had a schematic....
Disco
Posts: 14
Joined: Fri Jan 03, 2003 1:01 am
Contact:

Post by Disco »

I have a schematic. I'm not sure how to attach it.
User avatar
dacflyer
Posts: 4748
Joined: Fri Feb 08, 2002 1:01 am
Location: USA / North Carolina / Fayetteville
Contact:

Post by dacflyer »

if you have the schematic as a file.. click the bottom that says
"ADD IMAGE TO POST"
try that....
Dean Huster
Posts: 1263
Joined: Wed Dec 05, 2001 1:01 am
Location: Harviell, MO (Poplar Bluff area)
Contact:

Post by Dean Huster »

Is it a DC welder, i.e., has a rectifier built in so that it's always a DC output? A three-phase welder, like the 3-phase alternator in a car, makes for some pretty smooth DC as far as ripple goes as compared to either standard half-wave or full-wave rectification.

Dean
Dean Huster, Electronics Curmudgeon
Contributing Editor emeritus, "Q & A", of the former "Poptronics" magazine (formerly "Popular Electronics" and "Electronics Now" magazines).

R.I.P.
Disco
Posts: 14
Joined: Fri Jan 03, 2003 1:01 am
Contact:

Post by Disco »

Yes - it is a DC welder. You are right, the three phase is smoother. But if I run on single phase, I will have more ripple than on three phase.

dacflyer - I'm still trying to get a schematic in here some how. Not having much luck. I don't see an option to "add image to post". Sorry to be so dense. I haven't done much of this forum stuff. I'm still learning and I'm a little slow. Thanks for your help and patience.[/list][/list]
Disco
Posts: 14
Joined: Fri Jan 03, 2003 1:01 am
Contact:

Post by Disco »

OK - Hope this works.
Link to the schematic:
http://www.flickr.com/photos/22415457@N04/2159926133/

You can enlage it after it opens.

I think I can use just the "C" winding. Disconnect all of the primaries and secondaries of the "A" and "B" winding. This will cut down on the max current out, but I don't think that is a problem. This set up would allow the use of the high and low range outputs. The fan is 110 volts. I can feed it from a small transformer.
User avatar
dacflyer
Posts: 4748
Joined: Fri Feb 08, 2002 1:01 am
Location: USA / North Carolina / Fayetteville
Contact:

Post by dacflyer »

i been looking at this schematic,,but i cannot see where the mains transformer primaries are..i see all the secondaries..
User avatar
jwax
Posts: 2234
Joined: Mon Feb 09, 2004 1:01 am
Location: NY
Contact:

Post by jwax »

How about playing it safe and giving Hobart a call?
Disco
Posts: 14
Joined: Fri Jan 03, 2003 1:01 am
Contact:

Post by Disco »

Sorry - forgot to attach this page. This is the primary side. I will be using 240 vac.

http://www.flickr.com/photos/22415457@N04/[/img]

Thanks
User avatar
dacflyer
Posts: 4748
Joined: Fri Feb 08, 2002 1:01 am
Location: USA / North Carolina / Fayetteville
Contact:

Post by dacflyer »

ok, i looked at the schematic,, looking at the primary schematic you shown.. use fig. 1 to switch the welder over for 230 volt operation..
just change the jumpers as shown in fig.1 its that easy..

then your power connections should be as 120v - 0v - 120v = 240 volt

before it was 208v - 208v - 208v = 3phase

good luck