This has me puzzled - its also late here, so that might be the problem.
How does a timer like this http://www.smarthome.com/images/4253adgm.gif work - without a neutral connected to the timer. As in, when the light is off - the timer is still on, without a compleated circuit. Or is the power to the light very small.
Thanks :p
Timers without neutral
-
- Posts: 400
- Joined: Tue Dec 25, 2001 1:01 am
- Location: Bellingham, WA
- Contact:
Re: Timers without neutral
That's entirely possible. It's also bad form to have a load never completely disconnected. it's also possible that the timer is connected between line and ground- also bad form and incompatible with GFCI.
- dacflyer
- Posts: 4751
- Joined: Fri Feb 08, 2002 1:01 am
- Location: USA / North Carolina / Fayetteville
- Contact:
Re: Timers without neutral
the lamp provides the neutral to the timer..and there is a small ammount of current being sampled
many of Plug-n-Power / X10 moduals work this way for the wall switches and dimmers etc.
many of Plug-n-Power / X10 moduals work this way for the wall switches and dimmers etc.
Re: Timers without neutral
Thats what I thought - we actually disconnected the ground and it still worked. So, it didn't make sense immediatly that it could still have power with the lamp off - since there is no neutral in the timer.
Re: Timers without neutral
Just measure the voltage drop over the timercircuit when the lamp is on. You will then see if the timer 'steals' a small amount of the voltage. When the lamp is off, it will still be a small current through it, to supply the timer circuit.
TOK
TOK
Gorgon the Caretaker - Character in a childrens TV-show from 1968.